Re: Gypsum Blocks : with Aquamiser - more info required



Harry Whittle asked about reading gypsum blocks using 24 vac or other AC
voltage.

We have used gypsum blocks and stainless steel probes with the Turf Tech
"WaterWatcher" control unit (not to be confused with the WaterWatcher that
uses infrared technology).  We use 24vac.   One should not use DC to read
gypsum blocks, as the direct current can cause migration of cations toward
one of the electrodes, similar to the problem Harry discussed earlier with
his stainless probes.  This causes "polarization" and coating of the
electrode and eventual malfunction (manifested as an infinite resistance) of
the block.   Even when using 24 vac, there can be some polarization effect
if there are any ground voltage gradients between the sensor and the
control/excitation unit.  One can usually place a capacitor in series with
the ground leg to overcome this.  We've had some gypsum blocks in place that
are read continuously using 24 vac, with no ill effects, provided they are
protected from ground currents.

The benefit of gypsum blocks over stainless probes is that they are not as
sensitive to additions of fertilizer in coarse soils (medium and fine soils
are not so sensitive).  The disadvantage of blocks is that they may not
respond very quickly to drying in coarse soils, and they do dissolve over
time.  Also, in freezing soils, blocks may suffer some cracking and
premature aging.

We have found that (on medium/fine soils at least), that the stainless
probes provide the best response, with only a minor drift in readings with
changing soil temperature and fertility (EC) of soil.  This is not a problem
if the "target" or threshold point for irrigation is somewhere (say
half-way) between the "stress" point and field capacity.  This way, even
though the target point may drift some over time, as long as the water added
each irrigation is less than the difference between field capacity and the
target point,  the rooz zone will hold all of the water added.

Stainless probes, in freezing soils, need to be removed and reseated every
two to three years or so, if the freezing action creates a void or air
pocket between the probe and the soil.  This is not a problem if the probes
are inserted directly from the soil surface, as we do ours.

Rick Allen
Biological and Irrigation Engineering
Utah State Univ.
Logan, UT
AllenRic@cc.usu.edu

>
>I am interested in the effect of applying AC to the gyp blocks on a
>continous basis and am wondering what sort of range of resistances are
>obtained.  Are the blocks in the process of breaking down while the
>current is applied such that they cannot be energized continuously?  I
>am also looking for a commercial source of the blocks.  I would run my
>own tests but I'm generally lazy and don't want to needlessly repeat
>what others I'm sure have already done.

>Harry Whittle